04-15-2007, 07:58 AM #1
PVC water supply lines in crawlspace
Similar Threads:Last edited by Jeff Eastman; 12-19-2007 at 03:27 PM.
04-15-2007, 08:46 AM #2
Re: PVC water supply lines in crawlspace
From the IRC.
- P2904.5 Water-distribution pipe.Water-distribution piping within dwelling units shall conform to NSF 61 and shall conform to one of the standards listed in Table P2904.5.
- TABLE P2904.5
- - WATER DISTRIBUTION PIPE
- - - (PVC is not shown on the Table as an allowable material)
- P2904.4 Water service pipe.Water service pipe shall conform to NSF 61 and shall conform to one of the standards listed in Table P2904.4.
- TABLE P2904.4
- - WATER SERVICE PIPE
- - - Polyvinyl chloride (PVC) plastic pipe
The code reference, then, is "PVC is not allowed for use as distribution piping according to P2904.4 and Table P2904.5, IRC."
04-15-2007, 08:52 AM #3
Jerry may be right as to the code, but in NY the code also states that local law can over ride State and or National code. We have a large amount of CPVC piping and even some PVC piping that is labeled as use with potable water. That pipe in NY would not last one winter.
04-15-2007, 08:56 AM #4
*CPVC* is okay for use as supply/distribution piping.
It's the *PVC* that is not.
However, PVC *is* rated for use for potable water, which is why it is allowed outside for the water service pipe.
Are you sure that *PVC* is allowed for supply/distribution piping inside?