Thread: Flue clearance
04-11-2008, 01:30 PM #1
Flue clearance
Does a water heater flue pipe require the same 3-2-10 rule same as firplaces. For the life of me I cant find my reference.
Jim
04-11-2008, 01:59 PM #2
Re: Flue clearance
Do not have code but if closer than 8 feet to wall vent must extend 2 feet above roof.
04-11-2008, 01:59 PM #3
Re: Flue clearance
Jim, I'm not sure about that. But how close is that flue pipe to the adjacent roof surface? Is that type-B vent or single walled?
04-11-2008, 02:10 PM #4
Re: Flue clearance
That's single walled pipe. The pipe is almost touching the wood fascia. I have the one inch clearance from the roof sheathing but I dontThink I have one inch from the fascia. I'm also concerned about drafting properly.
Jim
04-11-2008, 02:16 PM #5
Re: Flue clearance
NFPA 54 12.7.2. Gas Vent Terminations.
A.........
B Gas vents that are over 12 inches in size or are located less than 8 ft. from a vertical wall or similar obstruction shall terminate not less than 2 ft. above the highest point where they pass through the roof and not less than 2 ft. above any portion of a building within 10 ft horizontally.
04-11-2008, 02:24 PM #6
Re: Flue clearance
Thanks david,
This site Rocks when I need it.
04-11-2008, 02:29 PM #7
Re: Flue clearance
04-11-2008, 02:30 PM #8
04-11-2008, 03:00 PM #9
Re: Flue clearance
My bad, That is a type B flue, however it is less than 12 inches in diameter. Does the same clearance from horizontal objects apply?
Jim
04-11-2008, 03:06 PM #10