    Default flue clearance and installation
    see any problem with the flue height etc on this roof.
    Noted this Bvent should be 1" to combustables as well right?
    OREP Insurance
    Aug 2007
    Memphis TN.
    Default Re: flue clearance and installation
    Quote Originally Posted by Jerome W. Young View Post
    Other than it's not at least 2 ft higher than any portion of the building within 10 feet ?
    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.
    Quote Originally Posted by Billy Stephens View Post
    Not counting the sloped roof, but referring to the wall nearby, right?
    Each slope roof has a minimum height above it, I believe it starts at 1 foot.
    Now, if that wall is within 8 feet, the gas vent needs to be 2 feet higher than the wall/roof at the wall.
    Of course, they are also supposed to be vertical too (just not sure how far off vertical is allowed where it comes out above the roof).
    Aug 2007
    Memphis TN.
    Quote Originally Posted by Jerry Peck View Post
    -- referring to the wall nearby, right?
    Oops,
    Single wall vent Reference IRC 2006 2427.7.3 = 10 feet